Electric motor insulation resistance test (megger)
Megger test of a motor winding: isolate and discharge, disconnect drives, choose the test voltage, measure phase-to-earth for 1 minute, correct for temperature, compare with the trend and acceptance limits, then restore.
11 stepsElectrical installationsVersion 2Updated
This template covers a high-hazard activity. Adapt it to your site’s written procedures, your equipment and local regulations, and have it approved by a competent person before use. When imported, it lands for review: a checklist as a draft, a procedure as inactive.
Free account — copy the procedure into your workspace, or download it as PDF or Excel.
Already have an account? Sign inWhat’s inside
Isolate and lock out the motor
Isolate the motor supply and apply locks and tags following your lockout / tagout procedure, then verify absence of voltage at the motor terminals.
Action15 minTools: Lockout devices, voltage tester
Risks: Electric shock and arc flash; wear the PPE required for the supply.
Discharge the windings
Connect each winding to earth to drain any stored charge, including from power factor correction capacitors, before touching the terminals.
Action5 minTools: Earthing lead
Risks: Windings and capacitors can hold a dangerous charge after isolation.
Disconnect the motor from cables and electronics
Open the terminal box and disconnect the supply cable. Never megger through a variable frequency drive, soft starter or other electronics: the test voltage destroys them. Disconnect surge capacitors and winding sensors, or test them separately.
Action20 minTools: Insulated hand tools
Risks: Test voltage applied to drive electronics or sensors damages them beyond repair.
Record motor data and winding temperature
Note the rated voltage and power from the nameplate, and measure the winding or frame temperature and the ambient humidity. Insulation resistance depends strongly on temperature.
Measurement5 minTools: Contact or infrared thermometer, hygrometer
Select the test voltage
Choose the DC test voltage from the motor’s rated voltage, following IEEE 43 practice or your site standard. Typical guidance: 500 V DC for motors rated up to 1000 V, 500–1000 V DC up to 2.5 kV, 1000–2500 V DC up to 5 kV.
Verification2 minTools: Insulation resistance tester (megohmmeter)
Measure phase-to-earth insulation for 1 minute
Connect the tester between the three phases tied together, or each phase in turn, and the motor frame earth. Apply the test voltage for 1 minute and record the value; where possible also record the 10-minute value to calculate the polarization index.
Measurement10 minTools: Insulation resistance tester, test leads
Risks: Terminals and cables carry the test voltage during the test; keep everyone clear.
Measure phase-to-phase insulation
Optional: where both ends of each winding are accessible, test between phases to detect inter-phase insulation weakness.
Measurement10 minoptionalTools: Insulation resistance tester, test leads
Correct for temperature and compare with the trend
Correct the reading to a common base temperature, usually 40 °C (resistance roughly halves for every 10 °C rise), and compare it with this motor’s previous results. A steady fall matters more than one value.
Verification10 minCheck against the acceptance limit
IEEE 43 minimum for the 1-minute value corrected to 40 °C: 5 MΩ for random-wound stators and for form-wound coils rated below 1 kV (most low-voltage motors); 100 MΩ for form-wound AC windings built after about 1970 (most medium-voltage motors); 1 MΩ plus 1 MΩ per kV of rated voltage only for windings built before about 1970 and for field windings. Use your site standard where it is stricter. Where measured, the polarization index should be 2 or more. Below the limit, do not return the motor to service: dry it out and retest.
Verification5 minRisks: Energising a motor with failed insulation can cause an earth fault, fire or electric shock.
Discharge the windings again
Earth the windings after the test for at least as long as the test voltage was applied, ideally four times longer, before touching the terminals.
Action5 minTools: Earthing lead
Risks: The winding stores charge from the test voltage.
Reconnect and restore the motor
Reconnect the cables to their marked terminals, tighten to the specified torque and close the terminal box with its gasket. Remove locks following your lockout procedure, restart and check the direction of rotation if connections were disturbed. Record all results.
Action20 minTools: Torque wrench, insulated hand tools
Reviews
No review yet.
Reviews come from companies that imported this template. Comments are checked before they are shown.
Questions about this template
Licence
Official FreeMaint template, free to use and adapt inside your FreeMaint workspace. An adaptation may be shared in the library under CC BY 4.0; its page then credits this template.
Templates are general guidance. They do not replace the manufacturer’s instructions, your site procedures or applicable regulations.
Equipment: Electrical installations
Industries: Manufacturing, Energy and utilities, Facilities
More templates for this equipment
- Inspection checklistOfficial FreeMaintSafety-critical
Electrical distribution board quarterly inspection checklist
Quarterly external visual inspection of an electrical distribution board by a competent person, covers kept closed: clear access, enclosure and door, warning signs and circuit labels, burning smell or discoloration, tripped devices, RCD test buttons and thermography follow-up.
17 checkpointsElectrical installations
- HSE checklistOfficial FreeMaintSafety-critical
Electrical work permit — isolation checklist
Checks to complete on each electrical work permit before work on a de-energised installation: authorised people, every source disconnected and locked, stored energy discharged, absence of voltage verified, earthing, adjacent live parts protected.
15 itemsElectrical installations