Electrical distribution board quarterly inspection checklist

Quarterly external visual inspection of an electrical distribution board by a competent person, covers kept closed: clear access, enclosure and door, warning signs and circuit labels, burning smell or discoloration, tripped devices, RCD test buttons and thermography follow-up.

17 checkpointsElectrical installationsVersion 1Updated

This template covers a high-hazard activity. Adapt it to your site’s written procedures, your equipment and local regulations, and have it approved by a competent person before use. When imported, it lands for review: a checklist as a draft, a procedure as inactive.

Use this template in FreeMaint

Free account: download it as PDF or Excel. Copying inspection checklists into your workspace is included from the Starter plan.

Already have an account? Sign in

What’s inside

Section 1 of 5

Safe conditions and access

  • Method — Inspection done with covers closed — no live work

    Pass / FailCritical risk
  • Access — At least 1 m clear in front of the board, nothing stored against it

    Pass / FailHigh risk
  • Room — Room or cupboard dry, no water ingress, not used for storage

    Pass / FailHigh risk

Section 2 of 5

Enclosure

  • Door — Door closes and locks; key held by authorised staff only

    Pass / FailHigh risk
  • Enclosure — Enclosure undamaged; no missing blanking plate or opening giving access to live parts

    Pass / FailCritical risk
  • Cable entries — Cable entries sealed, glands intact, no damaged cable sheath

    Pass / Fail

Section 3 of 5

Signs and labelling

  • Warning sign — Electrical hazard warning sign on the door

    Pass / FailHigh risk
  • Circuit chart — Circuit chart present inside the door and up to date

    Pass / Fail
  • Labels — Every protective device labelled legibly with the circuit it feeds

    Pass / Fail

Section 4 of 5

Signs of overheating or faults

  • Smell and noise — Any burning smell, buzzing or crackling from the board?

    Yes / NoNon-conforming answer: YesCritical risk
  • Discoloration — Any discoloration, scorch mark or melted plastic visible on the board?

    Yes / NoNon-conforming answer: YesCritical risk
  • Protective devices — Any breaker or RCD tripped without a known reason?

    Yes / NoNon-conforming answer: Yes
  • Indicators — Indicator lamps and meters, if fitted, show normal values

    Pass / Fail

Section 5 of 5

Tests and follow-up

  • RCD test — Warn the users of the affected circuits, press each RCD test button, then reset

    Done / Not doneHigh risk
  • RCD test — Every RCD tripped when its test button was pressed

    Pass / FailHigh risk
  • Thermography — Check the date of the last infrared survey under load and request one if overdue or a hot spot is suspected

    Done / Not done
  • Remarks — Defects for the electrician; RCDs that failed to trip

    Free textoptional

Reviews

No review yet.

Reviews come from companies that imported this template. Comments are checked before they are shown.

Questions about this template

Licence

Official FreeMaint template, free to use and adapt inside your FreeMaint workspace. An adaptation may be shared in the library under CC BY 4.0; its page then credits this template.

Templates are general guidance. They do not replace the manufacturer’s instructions, your site procedures or applicable regulations.