Electrical work permit — isolation checklist
Checks to complete on each electrical work permit before work on a de-energised installation: authorised people, every source disconnected and locked, stored energy discharged, absence of voltage verified, earthing, adjacent live parts protected.
15 itemsElectrical installationsVersion 2Updated
This template covers a high-hazard activity. Adapt it to your site’s written procedures, your equipment and local regulations, and have it approved by a competent person before use. When imported, it lands for review: a checklist as a draft, a procedure as inactive.
Free account: download it as PDF or Excel. Copying HSE checklists into your workspace is included from the Starter plan.
Already have an account? Sign inWhat’s inside
Category: Permit — pre-work checklist
- Permit type: Electrical
- Filled in on each permit concerned, before the work starts.
Imported as a draft: it is not used until you review it and click Activate on the HSE template. Once activated, it is used on every new permit of this type and replaces the checklist in use.
Checklist items
The work is done on a de-energised installation
Live working is not covered by this checklist: it needs its own authorisation and procedure. Live parts left nearby are dealt with below.
Pass / FailCritical: a failure blocks the permitVoltage level of the installation
ChoiceRequired- Low voltage
- High voltage
The people doing the isolation and the work are authorised for this installation and voltage level
Pass / FailCritical: a failure blocks the permitEvery source of supply has been identified
Including back-feeds, standby generators, UPS, solar panels, capacitor banks and control circuits fed from elsewhere.
Pass / FailCritical: a failure blocks the permitEvery source is disconnected by its isolating device
A device suited to isolation, with its open position verified, visible where possible. A stop button or a contactor is not an isolation.
Pass / FailCritical: a failure blocks the permitEvery isolating device is locked open and tagged
With the personal padlock of each person working, or through a group lockbox, and a tag giving name, date and reason.
Pass / FailCritical: a failure blocks the permitStored energy has been discharged
Capacitors and the DC bus of variable speed drives discharged, after the waiting time given by the manufacturer.
Pass / FailCritical: a failure blocks the permitThe voltage tester has been proven before and after the test
Checked on a known live source or a proving unit, then the absence of voltage is tested, then the tester is checked again.
Pass / FailCritical: a failure blocks the permitThe absence of voltage is verified on every conductor, at the place of work
Pass / FailCritical: a failure blocks the permitEarthing and short-circuiting applied where required
Always on high voltage; on low voltage where there is a risk of re-energisation or induced voltage. Answer « Pass » if not required.
Pass / FailCritical: a failure blocks the permitAdjacent live parts are protected or the work zone is marked out
Insulating screens, covers or barriers in place, and the limit of the work zone clear to everyone.
Pass / FailCritical: a failure blocks the permitProtective equipment and insulated tools suited to the voltage and the arc flash risk are worn during the verification
Pass / FailCritical: a failure blocks the permitIsolation points and lock numbers
Each isolating device opened and the number of each padlock fitted, so the isolation can be removed in full.
Free textRequiredPhoto of the locked isolation points
PhotooptionalRemarks
Free textoptional
Reviews
No review yet.
Reviews come from companies that imported this template. Comments are checked before they are shown.
Questions about this template
Licence
Official FreeMaint template, free to use and adapt inside your FreeMaint workspace. An adaptation may be shared in the library under CC BY 4.0; its page then credits this template.
Templates are general guidance. They do not replace the manufacturer’s instructions, your site procedures or applicable regulations.
Equipment: Electrical installations
Industries: Manufacturing, Facilities, Energy and utilities, Healthcare, Food and beverage
More templates for this equipment
- Inspection checklistOfficial FreeMaintSafety-critical
Electrical distribution board quarterly inspection checklist
Quarterly external visual inspection of an electrical distribution board by a competent person, covers kept closed: clear access, enclosure and door, warning signs and circuit labels, burning smell or discoloration, tripped devices, RCD test buttons and thermography follow-up.
17 checkpointsElectrical installations
- ProcedureOfficial FreeMaintSafety-critical
Electric motor insulation resistance test (megger)
Megger test of a motor winding: isolate and discharge, disconnect drives, choose the test voltage, measure phase-to-earth for 1 minute, correct for temperature, compare with the trend and acceptance limits, then restore.
11 stepsElectrical installations