PM planOfficial FreeMaint

Air handling unit quarterly preventive maintenance plan

Quarterly plan for an air handling unit: filters at their final pressure drop, fan, belts and motor current, coils, condensate drain, dampers and casing; bearing greasing twice a year, coil cleaning and frost protection test once a year.

11 tasksHVACVersion 1Updated

Use this template in FreeMaint

Free account — copy the plan into your workspace, assign it to your equipment and switch it on, or download it as PDF or Excel.

Already have an account? Sign in

What’s inside

Schedule

Every 3 months

  • Fixed calendar: the next date does not move with the completion date.
  • Work order window: 14 days
Estimated duration: 2 hPriority: Medium

Imported inactive and without equipment: assign it to your assets, set its start date (the first due date), check the intervals against the manufacturer’s manual, then switch it on.

Tasks at each service

  1. Check the filters and replace those at their final pressure drop

    Read the differential pressure across each filter stage and replace the filters that have reached the final pressure drop given by the filter manufacturer, or that are damaged or wet. Check that the frames seal with no bypass.

    Measurement20 min

    Tools: Differential pressure gauge

  2. Inspect the fan, its belts and its pulleys

    Check the impeller for dirt and damage, the belts for cracks, glazing and tension, and the pulley alignment. Replace worn belts as a matched set. On a direct-drive fan, check the motor mounts and the impeller fixing.

    Inspection20 min

    Risks: Isolate and lock out the fan, and wait for it to stop completely, before opening the fan section.

  3. Measure the fan motor current

    Measure the running current of the fan motor and compare it with the nameplate and the previous readings; a drop can reveal a slipping belt or a closed damper.

    Measurement10 min

    Tools: Clamp meter

  4. Inspect the heating and cooling coils

    Look for dirt on the face of the coils, flattened fins, corrosion and leaks at the headers and valves. Straighten bent fins with a fin comb.

    Inspection15 min

    Tools: Fin comb

    Risks: Stop and isolate the fan before opening the access doors or reaching inside the unit.

  5. Clean the condensate pan and check the drain

    Remove sludge and slime from the drain pan, check that it drains completely with no standing water, and that the trap is filled and the drain line is clear. Standing water in an air handling unit is a source of microbial growth.

    Action15 min

    Risks: Stop and isolate the fan before opening the access doors or reaching inside the unit.

  6. Check the dampers and their actuators

    Drive each damper through its full stroke from the controls and check that the blades open and close fully and the linkages are tight.

    Verification10 min
  7. Inspect the casing, the doors and the insulation

    Check that the access doors close and seal, the inside of the unit is clean and dry, and the internal insulation is intact and not shedding fibres.

    Inspection10 min

    Risks: Stop and isolate the fan before opening the access doors or reaching inside the unit.

  8. Grease the fan and motor bearings (regreasable bearings only)

    Apply the grease type and quantity given by the manufacturer; never over-grease. Skip bearings sealed for life.

    Action15 minoptionalonce every 2 services

    Tools: Grease gun

  9. Clean the coils

    Clean both faces of the coils with a low-pressure water spray or a coil cleaner suited to the fin material, rinsing towards the drain pan, then check that the pan drains.

    Action60 minonce every 4 services

    Risks: Isolate the fan and protect the motor and electrical parts from water.

  10. Test the frost protection

    Simulate a low temperature at the frost thermostat or sensor and check that the unit reacts as designed (fan stop, outdoor damper closed, heating valve open) and raises its alarm.

    Verification15 minonce every 4 services
  11. Restart and record the readings

    Restart the unit, check the supply air temperature and the absence of abnormal noise, then record every value in the work order.

    Verification5 min

Parts (indicative)

  • Set of filters, sizes and class of the unit × 1
  • Set of fan belts, references of the unit × 1

Tools (indicative)

  • Differential pressure gauge
  • Clamp meter
  • Belt tension gauge
  • Fin comb
  • Grease gun

Indicative list: on import it is written into the plan’s description, to link to your own inventory.

Reviews

No review yet.

Reviews come from companies that imported this template. Comments are checked before they are shown.

Questions about this template

Licence

Official FreeMaint template, free to use and adapt inside your FreeMaint workspace. An adaptation may be shared in the library under CC BY 4.0; its page then credits this template.

Templates are general guidance. They do not replace the manufacturer’s instructions, your site procedures or applicable regulations.

Equipment: HVAC

Industries: Facilities, Healthcare, Education, Hospitality, Manufacturing